This thread explains why a Megmeet Ethernet/IP module may not connect directly to a Fairino robot controller without an intermediate master device.
Status
Known answer. If both sides are configured as Ethernet/IP devices/adapters, they cannot establish a direct device-to-device control link. A scanner/master is required.
Typical situation
- A welding power source or module exposes Ethernet/IP as a device/adapter.
- The Fairino fieldbus card also works as a device/adapter in the intended setup.
- Both sides wait for a scanner/master, so no direct communication is established.
Practical solution
- Add a PLC or industrial controller that acts as the Ethernet/IP scanner/master.
- Let the PLC read/write data from both devices.
- Map only the required welding signals: start, stop, program number, current, voltage, ready, fault, etc.
- If the welding source supports Modbus TCP or digital I/O, those may be simpler alternatives.
Please reply with
- Exact Megmeet model/module
- Fairino fieldbus card type
- Whether you have a PLC in the system
- Signals you need to exchange